Journal ArticleDOI
TL;DR: In this paper, an arbitrary practical limit is proposed such that I 1.5 t is numerically not greater than 250 times the ampere rating of the circuit, which is achievable with commercially available equipment using simple time current band coordination.
Abstract: Laboratory tests of arcing faults trapped between a corner of a simulated steel housing and single or multiple bus bars were found to be reasonably reproducible and caused relatively consistent burning damage. Single phase 277-V arcing fault tests using spacings of 1 to 4 in from bus bars to ground at current levels of about 3000 to 26 000 A indicate that damage is proportional to I 1.5 t. In this ``ballpark'' arc voltage and arc length need not be known to predict probable maximum damage. For coordinated short circuit and ground fault protection, an arbitrary practical limit is proposed such that I 1.5 t is numerically not greater than 250 times the ampere rating of the circuit. Probable maximum burning damage in cubic inches of copper, aluminum, and steel is predicted based on the tests. The arbitrary limit is achievable with commercially available equipment using simple time current band coordination. Lower limits can be achieved using more sophisticated ground fault protection equipment.

50 citations


Journal ArticleDOI
TL;DR: In this paper, an on-line digital computer technique for the protection of a generator against internal asymmetrical faults is described, which relies on the detection of a second harmonic component in the field current at the onset of a fault in the armature winding.
Abstract: An on-line digital computer technique for the protection of a generator against internal asymmetrical faults is described in this paper. The proposed technique relies on the detection of a second harmonic component in the field current at the onset of a fault in the armature winding. Discrimination against external faults is achieved by monitoring the direction of the negative sequence power flow at the machine terminals. Tests have been conducted on a laboratory synchronous generator for various types of internal and external faults. Results show that the total time for internal fault detection and tripping is well within half a cycle of the 60 Hz signal. A simple extension to negative sequence relaying and loss of excitation relaying is proposed.

30 citations


Journal ArticleDOI
TL;DR: In this article, an on-line digital computer technique is used for differential protection of a synchronous generator, which provides fault detection and tripping well within half a cycle and is also capable of discriminating between internal and external faults.
Abstract: This paper presents an on-line digital computer technique used for differential protection of a synchronous generator. It provides fault detection and tripping well within half a cycle and is also capable of discriminating between internal and external faults. In the latter case, sufficient restraint signals are generated to overcome maloperation. Further, the scheme is highly reliable even with CT saturation due to heavy through faults on the generating unit. On-line tests using a laboratory synchronous generator show the results for different types of internal and external faults with varying fault incidence inception.

27 citations


Book
01 Jan 1977
TL;DR: Power system protection and switchgear as discussed by the authors, power system protection, switchgear, power system switchgear and switchboard, power switchboard and switch-board, switchboard power protection, switching-board power system.
Abstract: Power system protection and switchgear , Power system protection and switchgear , مرکز فناوری اطلاعات و اطلاع رسانی کشاورزی

20 citations


Journal ArticleDOI
V. Cook1
01 Feb 1977
TL;DR: In this article, the performance of both unswitched and switched distance protection schemes using polarised-mho relays on systems subjected to simultaneous faults is investigated, and differences in protection philosophies of British and Continental relay manufacturers are highlighted and a comparison is given for switched schemes employing overcurrent starter units.
Abstract: The paper considers the performance of both unswitched and switched distance protection schemes using polarised-mho relays on systems subjected to simultaneous faults. The disturbances considered are flashoverfaults to earth, cross-country earth faults and open-conductor plus earth faults on a double-circuit 132 kV transmission system. Consideration is also given to protection performance for double earth faults separatedby a star-delta transformer. Differences in protection philosophies of British and Continental relay manufacturers are highlighted and a comparison is given for switched schemes employing overcurrent starter units.

15 citations


01 Jan 1977
TL;DR: In this article, the authors provide an introduction, definitions, and basic theory development for electrical power systems, including power system protection, circuit interruption and switching overvoltages, stability of power systems; traveling waves in transmission lines; insulation coordination; rectification, inversion and highvoltage dc systems; 3-phase network matrices and coordinate system transformations; power system analysis; and aspects of system integration and development.
Abstract: This textbook is intended for university and technical students studying electrical power systems. Each chapter provides an introduction, definitions, and basic theory development. This volume contains information on power system protection; circuit interruption and switching overvoltages; stability of power systems; travelling waves in transmission lines; insulation coordination; rectification, inversion and high-voltage dc systems; 3-phase network matrices and coordinate system transformations; power system analysis; and aspects of system integration and development. Appendices on matrix algebra and the economics of electrical power generation are included. (LCL)

15 citations


Patent
08 Dec 1977
TL;DR: In this paper, the authors proposed a voltage limiter means such as back-to-back Zener diodes across each of the current transformers related to the phase and neutral conductors.
Abstract: In systems, such as aircraft electric power generation systems, three phase AC generators are often operated in parallel when supplying power to load busses and differential protection networks are utilized in each phase of each generator for detecting current imbalance between the phase conductor at the load and the neutral conductor of each phase. In this invention there is provided voltage limiter means such as back-to-back Zener diodes across each of the current transformers related to the phase and neutral conductors which, in conjunction with the other portions of the differential protection networks: (1) prevents nuisance tripping on the occurrence of high current faults outside the differential protection zone (such as bus faults) due to normal variations of the current transformers, and (2) at the same time, provides differential protection for a generator channel over the required range, generally from very low differential fault currents to the very high differential fault currents. The high differential fault currents will appear as high through current faults for the unfaulted parallel channels.

11 citations


Journal ArticleDOI
W. G. Schneeweiss1
TL;DR: In this article, the pdf of the duration of non-self-reporting faults is derived, and the pdf depends on the length of an item's life and the distance between checks.
Abstract: The pdf of the duration of hidden (non self-reporting) faults is derived. It depends on the pdf of item's life and the pdf of the distance between checks.

8 citations


Journal ArticleDOI
TL;DR: In this paper, the authors present a review of the more important basic electrical circuit analysis techniques used for determining the voltage and current relationships which describe various power system network events and operating conditions.
Abstract: Portions of the material proposed for a chapter in a new IEEE Standard (#399-the ``Brown Book'') being prepared by the Power System Analysis Subcommittee of the I & CPS Committee are presented. In order to establish a library of approved analytical methods, the material provides a review of the more important basic electrical circuit analysis techniques used for determining the voltage and current relationships which describe various power system network events and operating conditions. Certain simplified circuit arrangements are examined. They illustrate the power and merit of the analytical methods that evolve, as well as the errors that can occur because of improper regard for the restraints that apply. Using the analytical methods, the classical problem of a three-phase induction motor operating with one phase of the supply line open-circuited is studied in considerable detail. Finally, important observations and conclusions are presented regarding the motor protection requirements.

7 citations


Journal ArticleDOI
TL;DR: The design of the RPS-II and the operation of the micro-computer within the Reactor Protection System are described, which utilizes a micro- Computer to handle the more complex trip functions.
Abstract: Reactor Protection Systems for Nuclear Power Plants have traditionally been built using analog hardware This hardware works quite well for single parameter trip functions; however, optimum protection against DNBR and KW/ft limits requires more complex trip functions than can easily be handled with analog hardware For this reason, Babcock & Wilcox has introduced a Reactor Protection System, called the RPS-II, that utilizes a micro-computer to handle the more complex trip functions This paper describes the design of the RPS-II and the operation of the micro-computer within the Reactor Protection System

5 citations


01 Jan 1977
TL;DR: This volume contains information on power system protection; circuit interruption and switching overvoltages; stability of power systems; travelling waves in transmission lines; insulation coordination; rectification, inversion and high-voltage dc systems; 3-phase network matrices and coordinate system transformations; power system analysis; and aspects of system integration and development.
Abstract: This textbook is intended for university and technical students studying electrical power systems. Each chapter provides an introduction, definitions, and basic theory development. This volume contains information on power transmission; transmission line inductance; transmission line capacitance; overhead lines; underground cables; transformers; synchronous machines in power systems; power system fault calculations; and power system protection. (LCL)

Journal ArticleDOI
Rene Castenschiold1
TL;DR: In this article, the authors discuss various approaches that have been proposed to solve the ground-fault protection problem in electrical systems having alternate emergency or standby power, and place particular emphasis on code requirements and overall reliability of the electrical systems.
Abstract: Providing reliable ground-fault protection in electrical systems having alternate emergency or standby power can present serious problems unless adequate equipment is selected and properly coordinated. Multiple neutral-to-ground connections may prevent adequate sensing of ground-fault currents and may also cause nuisance tripping of circuit breakers. This paper discusses various approaches that have been proposed to solve these problems. Particular emphasis is placed on code requirements and overall reliability of the electrical systems.

01 Jan 1977
TL;DR: In this paper, a review of existing methods of generator and transformer fault protection of large units is presented and shortcomings pointed out, and various methods are compared in a qualitative manner and improvements suggested.
Abstract: Existing methods of generator and transformer fault protection of large units are reviewed and shortcomings pointed to. Various methods are compared in a qualitative manner and improvements suggested. Included are combustion detectors for the indication of incipient faults, installed inside the tank of transformers with nitrogen cushion on top.

Journal ArticleDOI
TL;DR: In this article, the authors outline problems experienced with high resistance faults on power system transmission lines and propose new techniques to detect high-resistance faults on the New South Wales power system.

Journal ArticleDOI
TL;DR: The equipment described contains several modules with variable input signals and auxiliary components together with a family of typical relay function cards used for protection experiments and final year projects.
Abstract: The equipment described contains several modules with variable input signals and auxiliary components together with a family of typical relay function cards. Provision is also made in the front panel for the design of standard or new types of relays using operational amplifiers. The unit is used for protection experiments and final year projects.